Looking for a tech that can come out and evaluate our usage by appliance. We are currently arguing with our HVAC company that our bill is sky-high because of a flaw with the heating system (10 months old - full warranty), but they are adamant it is not. I've reached out to a local electrician to see if they handle anything like this, but monitoring usage isn't really in their wheelhouse.Background for HVAC nerds: We've had HVAC company out for 6 service calls for cooling and heating not working in our new home. The air handler froze in the summer, the outside unit freezes now in the winter. They say it was all because of a collapsed hidden duct that was choking the air flow and they have now fixed it. Our energy bill is still very high after the fix and we are pretty sure it is running AUX Heat constantly - which they now say is normal sometimes and/or the thermostat may say that, but the Aux Heat isn't actually running. I've now seen it display Aux Heat running for 6+ hours and struggling to maintain Hold temp (thermostat always is set to Hold @ 71 degrees), while it is mid 50s outside, and the outside unit is not spinning or doing anything. Am I insane to think we are just running pure Aux Heat all the time? They insist it is not the HVAC system causing the spike in billing, but nothing else has changed or had issues. They've replaced duct work, replaced defrost board on unit, checked pressures/levels/balances, and basically said it is all perfect - they now say they will come check out our thermostats next.... as a courtesy - then they are pretty much done with helping us an we have to swallow $500 a month in electric bill...
1/31/2019 12:35:44 PM
What's the sq footage of your home? Just wanting to know for comparison purposes. Ours runs around 275/month between December and February, and our home is about 2300 sq ft, with 1 unit down and one unit up.We have a very old unit (17-18 yrs old) and we seem to be doing ok, albeit inefficient. Much better than your brand new unit. What kind of thermostat do you have? Obviously, these cold evenings are going to have your heat strips running all the time, but if you're at 50 outside, then your unit should be spinning. Do you have some type of attempt delay on your thermostat? Ours will attempt to run the heat pump for a certain amount of time before kicking on the aux heat.But something def. sounds wrong. What part of town are you located? I have a guy I definitely trust, if you're not too far from here.
1/31/2019 1:06:01 PM
You may want to keep track manually first before spending money on monitoring. Keep a log of when the heat goes on/off and the corresponding kwh meter reading. If you have a smart meter, your utility may have a monitoring application you can use.How much do you expect the HVAC to be each month?Definitely sounds like something's wrong though.
1/31/2019 1:15:56 PM
1/31/2019 3:31:34 PM
So I'm assuming you're heating via a heat pump? Gas isn't available? Just one heat pump or multiple units? That's a big house...I wonder if you have enough capacity. Who makes the heat pump and what size/tons is it?What was your average bill last winter? What's the average this winter?
1/31/2019 4:47:02 PM
1/31/2019 4:49:38 PM
What kind of HVAC unit do you have? Post the make and model. Do you have an emergency heat switch anywhere?
1/31/2019 6:09:56 PM
Post a pic of the thermostat wiring too.
1/31/2019 6:12:15 PM
Hire another company, dont tell them anything about the warranty
1/31/2019 8:13:42 PM
I feel like it's also worth asking how you found this company, and how prominent they are in the local biz.
1/31/2019 10:58:08 PM
it sounds like low refrigerant to me, that would explain the ice and the not able to reach the set temp and the increased aux heat usage
2/1/2019 7:46:13 AM
It's the company my custom builder contracted and they did the install. The levels have been "perfect" all 6 times they've been out. They're coming again next week and now my builder is insisting they cut us a check to cover the overage in our electric bill... We'll see how that turns out. I have an electrician coming to measure amperage and see if we can get any useful info from the panel.I may just buy a monitoring kit and have them hook it up for me at some point
2/1/2019 9:32:17 AM
They come out, say everything is ok again, and cut you a check for this month.What are you going to do next month?
2/1/2019 10:33:14 AM
There are only a few things that can run an electricity bill that high this time of year. A broken electric hot water heater, super bad insulation, or running the electric heat a lot.You know your Aux heat is running. You need to find out when and why.A collapsed duct will cause things to freeze up. It will also kill the compressor which I'm surprised didn't happen.Aux heat is supposed to run when: 1) It's really cold and the efficiency of the heat pump drops to shit. 2) When the heat set point is a lot higher than the current air temperature (usually 3 deg F). Check the paperwork that came with the unit. Then whole sequence of operations is explained in there.Maybe the thermostat is messing up. Maybe the controls are wired wrong. Maybe it's something elseSince it's new, the warranty likely covers parts and labor. Get on the manufacturers website, look up a manufacturer-certified local HVAC outfit, and call someone who knows what they're doing. Worst case, send the bill to your current incompetent people.
2/1/2019 1:15:22 PM
I guess my questions weren't interesting enough for mildew to answer [Edited on February 2, 2019 at 3:25 AM. Reason : Ok he did answer one ][Edited on February 2, 2019 at 3:27 AM. Reason : I have a good friend who works for the company you should have hired if you want me to hook u up with the good guys]]
2/2/2019 3:24:14 AM
2/4/2019 11:16:12 AM
2/5/2019 3:10:33 PM
On a 60 degree day, why is ANYTHING running ... open those damn windows and turn that thing off!! Seriously though, shouldnt run for more than a few minutes if its 60 degrees outside - unless your insulation is shit or you have a major blockage somewhere.I run ~100/month in the winter (thanks to my awesome wood stove). Keeps the house 75 all night long for the price of a couple large dry logs (free with labor).[Edited on February 5, 2019 at 4:12 PM. Reason : logs]
2/5/2019 4:10:47 PM
2/5/2019 6:17:44 PM
You're not wrong about the Aux heat running with the heat pump. They'll both run if the set temp is a lot lower than the inside temp. There are other cases where either the heat pump only or electric heat only will run depending on the make and model and how they're configured. This is why mildew needs to tell us what equipment he has.
2/5/2019 11:20:30 PM
2/6/2019 12:16:10 PM
Post the label for the outside unit too.Electric heat only is an option with your air handler. Post of pic of the thermostat wiring too. If there is an orange wire connected (assuming color codes were followed), you're not electric heat only.[Edited on February 6, 2019 at 1:47 PM. Reason : more info]
2/6/2019 1:41:22 PM
aux heat should only run by itself if you're in "emergency heat" mode (which is usually triggered by an equipment freezing incident or otherwise an issue with the heat pump). outside of that the heat pump pump should be running with the aux heat.]
2/6/2019 1:46:06 PM
^ The heat pump should run by itself without the Aux heat unless it can't keep up in which case it will also turn on the Aux heat. I'm still wondering if they have him set up to use the heat pump for heat.[Edited on February 6, 2019 at 1:51 PM. Reason : can't type]
2/6/2019 1:49:52 PM
2/6/2019 2:44:47 PM
2/6/2019 2:47:45 PM
What is your electric rate? Did you sign up for any alternative providers that are charging you more than normal? Are you able to compare your kWh usage with your neighbors that have a similar house?
2/6/2019 4:45:51 PM
Had an electrician out, No issues with overall house electric wiring or appliances drawing more amps then expected. He noticed the fan was running on HVAC constantly, and the heat wasnt, even though it was indicated on thermostat. Couldn't get downstairs heat to work at all. Upstairs would run ok, actually use the heat pump, when downstairs zone was off, but not with both on. He thinks something is wrong with wiring, thermostat, sensor, relays, or control board in the unit.
2/6/2019 6:23:52 PM
2/6/2019 6:27:40 PM
Outside unit
2/6/2019 6:32:09 PM
Downstairs therm
2/6/2019 6:41:13 PM
One of those wires is not like the others.Someone else will have to say whether or not that's significant.
2/6/2019 9:30:37 PM
If you were to disconnect that white wire from the thermostat and set your heat to run, just the heat-pump should run (It should do that anyway). Make sure you set your thermostat is set to heat and not emergency heat. The E and Aux are bridged, but I think that's ok. They both trigger the electric heat. Run through the system setup on page 8 of the thermostat manual. Make sure it's set for heat pump on Aux heat and electric heat on emergency heat.I noted that you seem to have a zoning kit. That makes all of your controls way more complex.If the heat pump won't run by itself, you have a problem and need it addressed.The label on the air handler says no heater is installed, but you can add the heat strips as supplementary kits so that doesn't mean there aren't electric heat strips in there. What's the breaker size? I would expect 30Amps or more.I'd call someone. It's worth $100 for piece of mind I would things. Make sure whoever you call knows about the zoning kit.For your reference:https://resources.lennox.com/fileuploads/Lennox_CBX25_IOM.pdfhttps://resources.lennox.com/fileuploads/b4c96de6-3b85-45dd-9083-6867b08cd43fLennox_14HPX_IOM.pdfhttps://customer.resideo.com/resources/techlit/TechLitDocuments/33-00000s/33-00141ES.pdf
2/7/2019 11:03:47 AM
any updates?
2/12/2019 10:59:51 AM
HVAC company has cancelled twice now, trying to get them out this week.Had Duke energy out, we have been using the equivalent of a 5,000+ sqft house according to them. They did the basic house assessment (It's free and I recommend everyone do it - they basically walk around with a heat camera and inspect insulated areas) and their recommendation is to have HVAC re-evaluated (SHOCKER!). The Duke guy did say he can't believe we didn't go for a natural gas heater - but we weren't given the option, most builders do electric bc it is cheaper install.
2/13/2019 10:11:09 AM
2/13/2019 10:58:38 AM
^^ the same HVAC company that installed, or another company? stop fucking with the company that installed this, get someone else to look at it
2/14/2019 9:09:09 AM
Mind sharing who you're hvac company is? I'm in so. wake too, I don't want to call out incompetence if Ellis isn't ever available.
2/14/2019 11:26:55 AM
^^ think he's still screwing with the same one. i advised him to do the same as you.[Edited on February 14, 2019 at 12:46 PM. Reason : they've been out like 5 times and cant fix. not they're cancelling on you repeatedly. can't even show up when they say they will]]
2/14/2019 12:45:30 PM
Updates?
2/18/2019 10:49:49 PM
They installed Nest thermostats to track usage, they now believe it was something with original thermostats and zoning. Now, we wait again. I did notice it seems to be running without using aux heat now. The outside unit spins up much more frequently.I don't want to call them out, yet... I have tried another company which won't come out since it's under warranty.
2/19/2019 10:16:39 AM
you need to not say anything about warranty to the other company
2/19/2019 10:56:34 AM
But the warranty will pay the other company? It doesn't matter who does the work so long as they're licensed. (Assuming a hardware problem and not an installer error.)
2/19/2019 1:21:56 PM
2/19/2019 1:51:22 PM
2/19/2019 3:06:26 PM
The warranty will cover parts and labor. If there's a hardware problem, the manufacturer takes care of everything. If it's an installation problem (which would include shenanigans with the zoning kit) then the warranty doesn't apply. I'd take that bill to the original people and make them eat it.Fun aside, I made a warranty claim when I replaced the gas valve in my own HVAC system myself. I actually made money on that deal since they covered the part and my labor.
2/19/2019 3:23:38 PM
For anyone still interested.... Had 7 hours yesterday were both Nests indicated heat was running (set to hold 71 degrees on each) but the actual temp never got above 67 - the heat pump was not running during any of this nor were the heating coils. "Heat" was actually just the fan blowing cool air for 7 hours. I tried turning the breaker off and on to see if we could get anything by resetting it (it was pretty cold in kid's rooms at bed time and I was desperate) - after a few minutes post-reset everything worked as expected. The HVAC guy was actually monitoring it during that time and today they have now promised to replace the entire unit.... We are trying to push for a gas heater.
2/22/2019 12:50:30 PM
Yeah I would definitely push for a different company.
3/22/2019 2:09:37 PM
3/22/2019 3:52:50 PM
news?